    Not only do you need a 60 amp breaker but you also have to consider wiring size depending on the run. 8awg for the first 5′ up to 2awg for runs of 25′

    That’s exactly it. Thanks! I was talking to the tech who converted the system for me. He just left in the breaker that was there for the 12v system. Idiot. So he’ll be putting in a 60 amp breaker. AND he’ll check to see what gauge the wiring is. It doesn’t run more than 5 feet, but I’m not sure it’s even 8 AWG.

    Should be good to go after these modifications!

    DC Cougar
    Posts: 6
    #2292880

    Thanks, guys! I gotta check what amp breaker was put in previously…..