Since you are all on the topic, I’m wondering if 14 guage is the right wire for a 24 v motorguide xi5 80 lb, I’m not sure I’m understanding the chart gizmo posted.
NO! to read the chart you need to know the max amps that your motor can draw AND the length of the wires between the batteries and the motor. First find your amp number in the far left column in the chart. From that number and on the same line as that number, move along to the right until you get to a number equal to or greater than the length of the wires. From the wire length number in the chart move back straight up and at the top of the column, you will find the wire size you need to use.
as an example lets assume your motor draws 50 amps and the wire length you need is 15 feet.
Going down the left hand column we find 50 amps at the bottom line. Moving to the right we find 13 feet, not enough. Next number is 21 feet, yes that is long enough. Moving straight up that column at the top we read the number 6 and we have our answer.
6 gauge wire will safely carry 50 amps over a distance of 21 feet. If we needed to reach 23 feet then we would need to increase our wire size to 4 gauge wire.