HVAC Question

  • Geerdes
    Brandon, SD 57005
    Posts: 791
    #1895912

    I have Reznor garage furnace. The fan kicks on but the igniter clicks and won’t light and then it clicks and tries to light but won’t. Any suggestions?

    Gregg Dillenburg
    Posts: 5
    #1895916

    I’ve had that happen. It’s the thermo couple. You can try and clean it if you are lucky. Just take some emery paper to it where the pilot hits it. Otherwise you will have to change out the thermal coupler. Pretty easy to do.

    Loren I Duerr
    Posts: 114
    #1895919

    if it clicks as you say it does not have a pilot or a thermocouple it has an ignitor that is burned out. replace ignitor,

    munchy
    NULL
    Posts: 4928
    #1895920

    If it’s not lighting at all then it likely not the thermocouple. But you can try to clean it. Find the igniter and see if you can see a spark coming from it.

    dwalton
    Posts: 42
    #1895933

    Usually if you can hear it clicking, the igniter is sparking. Sounds like it’s not getting gas. Maybe bad solenoid, or control board not telling the solenoid to open the valve.

    Don Carlisle
    Aitkin mn
    Posts: 335
    #1895941

    It’s in what they call a soft lock out try shutting off the power for a minute. See if the pilot lites then.If the pilot is off and won’t stay on clean the flame sensor with fine steel wool

    Pauleye
    Onamia
    Posts: 276
    #1895945

    Usually if you can hear it clicking, the igniter is sparking. Sounds like it’s not getting gas. Maybe bad solenoid, or control board not telling the solenoid to open the valve.

    X2
    Can’t say it any better.

    Dave maze
    Isanti
    Posts: 976
    #1895948

    There could be quite a few things wrong. You need to have someone qualified look at it.

    Geerdes
    Brandon, SD 57005
    Posts: 791
    #1896170

    Took out igniter and sensor. Cleaned both and works great now. Thanks