permanent fish house and sonars???

  • BBKK
    IA
    Posts: 4033
    #1132514

    Bubbles being released from the bottom I bet. Pop some holes out around it and see if you still see them.

    mark-bruzek
    Two Harbors, MN
    Posts: 3921
    #1132523

    Fan motor running?

    Just to clarify you cut ALL power completely and tried each unit solo at this time?

    If you are still having issues I live on the lake, PM me a phone # and I can probably swing by tomorrow morning.

    thegun
    mn
    Posts: 1009
    #1132526

    Quote:


    Bubbles being released from the bottom I bet. Pop some holes out around it and see if you still see them.


    x2

    kwmagic
    Rochester, MN
    Posts: 40
    #1105935

    are your transducer pucks at the bottom of the ice?? I thought I had a vexilar issue once but it was cause from the trancducer still being surrounded by ice !!

    johnksully
    Lakeville, MN
    Posts: 678
    #1106008

    We figured out it is the generator. As soon as we unplug the generator from the outlet on the outside of the house everything works fine. Even with the generator still running.

    So there must be feedback coming through the electrical lines in the ice house???

    Any ideas?

    johnksully
    Lakeville, MN
    Posts: 678
    #1132613

    Problem solved. Had open grounds in the electrical panel.

    Denny O
    Central IOWA
    Posts: 5911
    #1132687

    Just thinking outloud here,
    If you have open grounds in the panel, I would go through the whole system box by box, fixture by fixture and check it all out. jmo.

Viewing 7 posts - 1 through 7 (of 7 total)