Battery wiring Ofc or cca?

  • fish-them-all
    Oakdale, MN
    Posts: 1189
    #2057941

    I ordered wire not realizing it was cca. Will that be ok or should get Ofc or tinned copper? I am upgrading to 8 gauge wire for a 24 volt trolling motor.

    Denny O
    Central IOWA
    Posts: 5827
    #2057942

    Personally I will not use copper clad aluminum. First I believe it will need to be a larger gauge size to start with.

    A highest number of copper strands for the same wire gauge that are tinned is best.

    Hot Runr Guy
    West Chicago, IL
    Posts: 1933
    #2057967

    As Denny mentioned, you need to up-size if using aluminum. Below are the results of a typical bow wiring scenario, 8′ run at 55amp (max). The voltage drop using aluminum is 2X that of copper.
    https://www.powerstream.com/Wire_Size.htm

    HRG

    Attachments:
    1. 8awg-alum.jpg

    2. 8awg-copper.jpg

    fish-them-all
    Oakdale, MN
    Posts: 1189
    #2057977

    Cool, thanks for the replies. Luckily I only ran wire under the front deck a few feet before checking. Unfortunately it was an area I had to fish it through. Back to the fun of boat rigging once I get new wire.